Just in case anyone in the future ever needed to connect the Konnected Interface Kit to their Bosch alarm I wanted to share the steps I took. The result is that I can via smartthings remotely arm (stay) and disarm (both stay or away), get notified whenever the alarm is armed (stay) or armed (away) and also when the alarm is triggered. Now I can cancel the back to base monitoring.
Please do your research before proceeding. Go through the konnected video installation guide a few times, read the installation manual of your alarm and also use AI to help though be careful as AI was not always right. Note that the steps I took slightly differs to the konnected video installation guide and so my steps may be different for you if you have a different alarm panel and also if your setup is different. If there are questions happy to answer. Hope this helps someone!
My alarm has 4 zones, 2 programmable outputs, 1 strobe output. Each zone originally has one PIR. I knew I had to free one of the zones so I moved one of the PIRs to another zone so that zone had 2 PIRs (which I had to wire in series and remove one of the extra resistor).
Remove PIR from Z4 and Adding to Existing PIR on Z3
· Power off system and remove backup battery
· Wire the two PIRs in series by removing Z3 blue wire and Z4 white wire from alarm panel and connect together.
· Rumpus PIR - Remove resistor, move blue wire from T to NC terminal
· Power on system THEN plug in RED connector to backup battery then Black connector to avoid sparks.
· Disable Z4 - Change location 288 from 0 to 15 (disabled)
Install Konnected Interface Kit
· Power off system and disconnect backup battery
Connect Alarm Panel to Interface Module
· Connect Alarm Panel Z1 to Z3 to Interface Module Z1 to Z3
· Connect Alarm Panel (STR = strobe) to Interface Module Z5
· Connect Alarm Panel (Programable Output 1) to Interface Module Z4
· Connect Alarm Panel (Programable Output 2) to Interface Module Z6
Connect Keyswitch
· Connect Alarm Panel Z4 to 3K3 resistor (taken from Rumpus PIR) to Interface Module (Relay)
· Connect +12V (Same terminal as Blue Wire of PIRs) to Interface Module (Relay).
· Polarity does not matter for Interface Module (Relay)
Connect Interface Module to Add-On
· Connect ribbon from Interface Module to Add-On
· Connect wire from IN (Interface Module) to OUT (Add-On)
Connect Power
· Connect Red wire from Alarm Panel (+12V) to Interface Module (VREF)
· Connect Black wire from Alarm Panel (GND) to Interface Module (GND)
· Connect Red wire of Power Splitter to Alarm Panel (+12V)
· Connect Black wire of Power Splitter to Alarm Panel (GND)
Tune Potentiometer
Note: The video tutorial was to turn counter-clock wise till led just goes out then turn clock wise so that the led just turns on. But when I did this the zone led did not turn off when there was motion. However, I noticed that when i tuned the potentiometer so that they just goes out then when there is motion the led would light up. Not sure why this happens but maybe the alarm panel is different to the one in the Konnected video installation guide. As a result of this when I setup the Interface Kit on the Konnected App I had to select the “Inverse” option.
· For Z1 to Z3 - Turn counter-clock wise till led just goes out.
· For Z4 - Regardless of how I tuned it the led light stayed on. Then as per video instruction i turned it counter clockwise to as far as it would go. The Z4 led stayed turned on → this was originally when I programmed Z4 via Programmable Output 1 to report Armed/Disarmed status. Since I subsequently changed Z4 via Programmable Output 1 to report Armed Away status I may have tuned the potentiometer again. When I got it working, the led light is normally on.
· For Z5 – Regardless of how I turned it the led light stayed on and no open or close change would register on Smartthings and so I think I just left the potentiometer in the middle but then when I changed the Event Code (eg Locations 368 and 369) then the sensor would open and close. Therefore, if tuning the potentiometer does not turn off the led light try changing the Event Code. Once I got it working the led light is normally off.
· For Z6 – I can’t remember how I tuned it but when I got it working it is normally on.
· In summary, once I got all everything working:
Ø The led lights on Z1 to Z1 and Z5 are normally off. This is also reflected in smartthings where they are normally closed.
Ø The led lights on Z4 and Z6 are normally on. This is also reflected in smartthings where these two devices (ie Armed (Away) and Armed (Stay)) are normally open.
Enter Alarm Panel Programming
· Click “Settings”, “Installation” and “Panel (enhanced)”. Enter Installer Code.
Program Programmable Output 1 which is connected to Z4 (to report Armed Away)
· Change location 368 to 0 (previously 1)
· Change location 369 to 4 (previously 14)
· Change location 370 to 1 (previously 0)
· Change location 371 to 0 (previously 0)
· Change location 372 to 0 (previously 0)
· Change location 373 to 0 (previously 0)
Program Programmable Output 2 which is connected to Z6 (to report Armed Stay)
· Change location 374 to 0 (previously 2)
· Change location 375 to 2 (previously 7)
· Change location 376 to 1 (previously 10)
· Change location 377 to 0 (previously 2)
· Change location 378 to 0 (previously 1)
· Change location 379 to 0 (previously 5)
Program Z4 as Keyswitch
· Change location 288 to 11 (previously 15)
· Change location 289 to 0 (previously 0)
· Change location 290 to 0 (previously 0)
· Change location 291 to 8 (previously 1)
· Change location 292 to 4 (previously 15)
· Change location 293 to 0 (previously 1)
· Change location 294 to 0 (previously 1)
Program STR
· No change needed as it was already connected to the strobe.
· I was run the strobe test under “Diagnostic” via the control touch panel to confirm the Interface module was correctly registering when the strobe was activated.
Setup in Konnected App
· Install Konnected app
· Add Konnected alarm panel but app was a bit buggy. Note the alarm panel only supports 2.4ghz wifi.
· Setup zones as follows:
Ø Zones 1 to 3 - Select “Motion” as zone type and click on “Inverse”
Ø Zone 4 - Select “Door” as zone type. Click on “Inverse”. Named as “Armed (Away)”
Ø Zone 5 – Select “Door” as zone type. Click on “Inverse”. Named as Strobe.
Ø Zone 6 – Select “Door” as zone type. Click on “Inverse”. Named as “Armed (Stay)”.
Ø Alarm/Out - Select “Momentary Switch” as zone type, 1000 ms as duration and leave Pause and Repeat as blank.
· Then click “Sync to Device”
Connect to Smartthings
· Connect Konnected as a service in Smartthings
· There should be a total of 7 devices:
(1) Entry
(2) Living Room
(3) Upstairs
(4) Strobe – Normally closed. If opened means the strobe is on and so is the alarm.
(5) Armed (Away) – Armed (Away) is activated when both “Armed (Away)” and “Armed (Stay)” are closed.
(6) Armed (Stay) – Armed (Stay) is activated when “Armed (Away)” is open and “Armed (Stay)” is closed.
(7) Arm/Disarm – This button activates “Armed (Away)” but can also deactivate “Armed (Away)” and “Armed (Stay)”.
Note: Alarm is disarmed when both “Armed (Away)” and “Armed (Stay)” are open.